Did they cut the wood with a Slabmizer?
New generator project. Between the hassle of renting (if I can find one) or dealing with coolers to save the food, it was time to finally get one.
I ordered this https://www.amazon.com/dp/B099KTG83R/?tag=wranglerorg-20 on an early Black Friday sale for $400. 7500 running and 9500 peak watts.
Power priority is
1) 2 fridges
2) HVAC. We have two units, the original gas furnace & 4ton AC which service the entire house and a heat pump with 2.5Ton unit which only services the upstairs. My thought for heat is to use the whole house gas furnace (blower motor should be low draw) and for AC only the newer 2.5T unit. Specs on the 2.5T compressor are 13.5A running and 72.5LRA which is over capacity but I’ve been reading about soft start devices and this looks like it should bring the startup draw in range. https://www.amazon.com/dp/B08YJK9MB3/?tag=wranglerorg-20
3) misc lights, internet.
I’ve got a main disconnect already, so plan would be to run a dedicated 220 circuit from the generator to the panel for input.
Open to feedback on 1) not starting a fire 2) not blowing my devices.
Current panel
The soft start is worth a try, you could even try it now off of normal AC power and see how it runs. Some compressors need all the inrush current to start successfully . So this is all manual with out an ATS ?
Power priority is
1) 2 fridges
Current panel
Power priority is
1) 2 fridges
Current panel
Don't try to run soft start devices if it will hurt the compressor. Capacitors are usually used for startup amps if the circuit can't handle it
Power priority is
1) 2 fridges
Current panel
Code in most locations requires an interlock if you don't have an ATS. This is mine.
Either the main breaker or the generator feed can be closed, but not both. This way there's no possible way for me to back feed the grid and blow up my meter or worse, kill a line worker.
Don't just wire a 220V outlet, look for a generator inlet, like this.
Kohree 50Amp Generator Power Inlet Box, NEMA SS2-50P for 3R Generator Cord Receptacle, 125/250V,12500W RV Weatherproof Generator Transfer Switch Inlet Box, ETL Listed https://www.amazon.com/dp/B08X1QNGJG/?tag=wranglerorg-20
That way you don't have to do any cowboy stuff...
Look for one made for your HVAC - I think its just a cap.Will add lockout to the list. . Tell me more about not blowing the motor using a soft start, is there a spec I should look for?
Yes to generator outlet, was looking at something like this.
You want the soft start on the A/C - although for some reason, my HVAC guys call it a "hard start". Its easy enough to install one. I have a 3 ton on a 15KW. The generator runs the A/C fine - BUT - before I put the soft start on, when the A/C started, there's be a pretty loud BANG! from the generator! It doesn't do that any more with the soft start in place.
Different things.
A soft starter is solid state device that ramps up the supply to the motor over a few seconds after start. A hard start is a capacitor that stores energy to supply the inrush to the motor without demanding it from the supply.
Both are used for the purposes of reducing the line-side current, they just do it in different ways. I typically see soft starters a lot more on 3-phase motors.
Different things.
This is the soft start I was looking at.
[URL]https://www.micro-air.com/supp...n_resources/EasyStart_Specification_Sheet.pdf[/URL]